Stand along upright freezer would not get below 16 degrees. I pulled off the evaporator cover. The drain plug, and the entire drainage area was frozen about 3/4 inch thick for the entire length of the back of the freezer. The water was also freezing on the inside of the bottom of the freezer.
The evaporator was very frosty, especially at the top and bottom. Even the evaporator cover in the middle had frost on it. Some parts were even icy.
In the back of the freezer, near the condenser, the drain tube that connects the above mentioned area to the drain pan was not connected. If the water were to drain, it would drain onto the floor.
I removed all the ice and frost then checked the drain tube. Water is draining.
Stand along upright freezer would not get below 16 degrees. I pulled off the evaporator cover. The drain plug, and the entire drainage area was frozen about 3/4 inch thick for the entire length of the back of the freezer. The water was also freezing on the inside of the bottom of the freezer.
The evaporator was very frosty, especially at the top and bottom. Even the evaporator cover in the middle had frost on it. Some parts were even icy.
In the back of the freezer, near the condenser, the drain tube that connects the above mentioned area to the drain pan was not connected. If the water were to drain, it would drain onto the floor.
I removed all the ice and frost then checked the drain tube. Water is draining.
Any idea why it is freezing up and not draining?
Thanks.
— End quote
Scottu,
The issue could be due to the disconnected drain line. Your freezer would have been "sucking" hot air off the compressor area and up into the evaporator area, cold air meets hot air equals frost and or ice. You could have a defrost heater or thermostat problem, but I would wait a while to see if the ice/frost reappears.
I posted the photo above which was before I defrosted.
Looking at it, do you still think it may be as simple as the hot air going into the drain hole? Could it be a thermostat or heater or other item? Thanks.
— End quote
Scottu,
Thanks for the photo, Now, I’m as sure as I can be, I seriously doubt you have a defrost problem. Only other thing you may want to check is, the freezer door seal. Make sure the seal is soft, clean and seals against the front flange when the door is closed, especially along the bottom.
It has been running about 8 hours completely assembled, and maintaining a good temperature. The channel in the back under the evaporator that the water uses to drain out already has some ice in it. Is this normal?
Basically the area that was totally iced up has started to develop more ice.
I’m not familiar with how it should work so this could be normal.
Thanks, Scott
— End quote
Scott,
The lower area of the freezer, is the coldest area, Some (minimal) ice would be normal. Keep an eye on it for a few more days, I think you’ll be fine.
Wife started washer,then pulled button out to stop.Put more clothes in and restarted.Made a funny humming noise,then promptly filled the house with smoke…What can I check?
Remove the front panel by inserting a putty knife into the top groove in line with the lid opening on each side to release the clips. Tilt panel outward and lift away from cabinet. Inspect the motor and motor connector/wiring for signs of overheating (smell for odor). Open control panel and inspect motor start capacitor (black cylinder).